Figure 1 - End of Row design
Server cabinets (or racks) are typically lined up side by side in a row. Each row might contain, for example, 12 server cabinets. The term “End of Row” was coined to describe a rack or cabinet placed at either end of the “server row” for the purpose of providing network connectivity to the servers within that row. Each server cabinet in this design has a bundle of twisted pair copper cabling (typically Category 6 or 6A) containing as many as 48 (or more) individual cables routed to the “End of Row”. The “End of Row” network racks may not necessarily be located at the end of each actual row. There may be designs where a handful of network racks are placed in a small row of their own collectively providing “End of Row” copper connectivity to more than one row of servers.
For a redundant design there might be two bundles of copper to each rack, each running to opposite “End of Row” network racks. Within the server cabinet the bundle of copper is typically wired to one or more patch panels fixed to the top of the cabinet. The individual servers use a relatively short RJ45 copper patch cable to connect from the server to the patch panel in the rack. The bundle of copper from each rack can be routed through over head cable troughs or “ladder racks” that carry the dense copper bundles to the “End of Row” network racks. Copper bundles can also be routed underneath a raised floor, at the expense of obstructing cool air flow. Depending on how much copper is required, it is common to have a rack dedicated to patching all of the copper cable adjacent to the rack that contains the “End of Row” network switch. Therefore, there might be two network racks at each end of the row, one for patching, and one for the network switch itself. Again, an RJ45 patch cable is used to link a port on the network switch to a corresponding patch panel port that establishes the link to the server. The large quantity of RJ45 patch cables at the End of Row can cause a cable management problem and without careful planning can quickly result in an ugly unmanageable mess.
Another variation of this design can be referred to as “Middle of Row” which involves routing the copper cable from each server rack to a pair of racks positioned next to each other in the middle of the row. This approach reduces the extreme cable lengths from the far end server cabinets, however potentially exposes the entire row to a localized disaster at the “Middle of Row” (such as leaking water from the ceiling) that might disrupt both server access switches at the same time.

Figure 2 - Middle of Row variation of End of Row
The End of Row network switch is typically a modular chassis based platform that supports hundreds of server connections. Typically there are redundant supervisor engines, power supplies, and overall better high availability characteristics than typically found in a “Top of Rack” switch. The modular End of Row switch is expected to have a longer life span of at least 5 to 7 years (or even longer). It is uncommon for the end of row switch to be frequently replaced, once its in – “it’s in” – and any further upgrades are usually component level upgrades such as new line cards or supervisor engines.
The End of Row switch provides connectivity to the hundreds of servers within that row. Therefore, unlike Top of Rack where each rack is its own managed unit, with End of Row the entire row of servers is treated like one holistic unit or “Pod” within the data center. Network upgrades or issues at the End of Row switch can be service impacting to the entire row of servers. The data center network in this design is managed “per row”, rather than “per rack”.
A Top of Rack design extends the Layer 2 topology from the aggregation switch to each individual rack resulting in an overall larger Layer 2 footprint, and consequently a larger Spanning Tree topology. The End of Row design, on the other hand, extends a Layer 1 cabling topology from the “End of Row” switch to each rack, resulting in smaller and more manageable Layer 2 footprint and fewer STP nodes in the topology.
End of Row is a “per row” management model in terms of the data center cabling. Furthermore, End of Row is also “per row” in terms of the network management model. Given there are usually two modular switches “per row” of servers, the result of this is far few switches to manage when compared to a Top of Rack design. In my previous example of 40 racks, lets say there are 10 racks per row, which would be 4 rows each with two “End of Row” switches. The result is 8 switches to manage, rather than 80 in the Top of Rack design. As you can see, the End of Row design typically carries an order of magnitude advantage over Top of Rack in terms of the number of individual switches requiring management. This is often a key factor why the End of Row design is selected over Top of Rack.
While End of Row has far less switches in the infrastructure, this doesn’t necessarily equate to far less capital costs for networking. For example, the cost of a 48-port line card in a modular end of row switch can be only slightly less in price (if not similar) to an equivalent 48-port “Top of Rack” switch. However, maintenance contract costs are typically less with End of Row due to the far fewer number of individual switches carrying maintenance contracts.
As was stated in the Top of Rack discussion, the large quantity of dense copper cabling required with End of Row is typically expensive to install, bulky, restrictive to air flow, and brings its share of cable management headaches. The lengthy twisted pair copper cable poses a challenge for adopting higher speed server network I/O. For example, a 10 gigabit server connection over twisted pair copper cable (10GBASE-T) is challenging today due to the current power requirements of the 10GBASE-T silicon currently available (6-8W per end). As a result there is also scarce availability of dense and cost effective 10GBASE-T network switch ports. As the adoption of dense compute platforms and virtualization quickly accelerates, servers limited to 1GE network I/O connections will pose a challenge in obtaining the wider scale consolidation and virtualization capable in modern servers. Furthermore, adopting a unified fabric will also have to wait until 10GBASE-T unified fabric switch ports and CNA’s are available (not expected until late 2010).
10GBASE-T silicon will eventually (over the next 24 months) reach lower power levels and switch vendors (such as Cisco) will have dense 10GBASE-T line cards for modular switches (such as Nexus 7000). Server manufactures will also start shipping triple speed 10GBASE-T LOM’s (LAN on Motherboard) – 100/1000/10G, and NIC/HBA vendors will have unified fabric CNA’s with 10GBASE-T ports. All of this is expected to work on existing Category 6A copper cable. All bets are off however for 40G and beyond.
Summary of End of Row advantages (Pro’s):
-Fewer switches to manage. Potentially lower switch costs, lower maintenance costs.
-Fewer ports required in the aggregation.
-Racks connected at Layer 1. Fewer STP instances to manage (per row, rather than per rack).
-Longer life, high availability, modular platform for server access.
-Unique control plane per hundreds of ports (per modular switch), lower skill set required to replace a 48-port line card, versus replacing a 48-port switch.
Summary of End of Row disadvantages (Con’s):
-Requires an expensive, bulky, rigid, copper cabling infrastructure. Fraught with cable management challenges.
-More infrastructure required for patching and cable management.
-Long twisted pair copper cabling limits the adoption of lower power higher speed server I/O.
-More future challenged than future proof.
-Less flexible “per row” architecture. Platform upgrades/changes affect entire row.
-Unified Fabric not a reality until late 2010.
credit to source